When running the CR0200 in extended mode (one master processor) only the outputs on PLC1 can be used for OUTPUT_CURRENT_CONTROL (OCC). The extended IO is not available for current control. This is because we want to limit the number of simulataneous OCC to 8. More than 8 could put an excessive load on the processor and cause long PLC cycle times.

If you need more than 8 OCC on the CR0200, you will need to run it as two processors and use the internal communication bus to pass values from PLC1 and PLC2.