    hi I am implement CAN network variable between CR0032 to safety PLC cr7506.

    data is transmit from the cr7506 and receive in the cr0032.

    Also data is transmit from the cr0032 but the data is not received in the cr7506
    I check the COB-ID in both side and it seems to be correct

    Is there a function block that I need to use? or configuration that I need to do?

    thank you in advance

  2. #2
    Join Date
    Oct 2016
    Posts
    22

    Default

    I understand the problem

    For receive lists you must also map the identifier area in the object directory to receive PDOs. It
    is sufficient to create only two receive PDOs and to assign the first object the first identifier and
    the second object the last identifier.