Results 1 to 3 of 3

Thread: Gateway Configuration

  1. #1
    Join Date
    Jun 2016
    Posts
    6

    Default Gateway Configuration

    I have a new installation of CoDeSys 3.5 and I'm having some trouble configuring the gateway properly to connect to a CR1201. The device is running OS v3.3.0.0 Repack 04, and the ethernet is is configured with the default manual settings:

    IP Address 192.168.82.247
    Netmask 255.255.255.0
    Gateway 192.168.82.1

    The computer's network adapter is configured with an IP address of 192.168.82.246, and all other network adapters have been disabled. I can connect to the device via a standard FTP client, just not with CoDeSys. "Scan Network" does not return any devices, and restarting the gateway service has no effect as well. Additionally, I've tried two software installations:

    SP15 Patch 1
    package ifm ecomatDisplay Products ***Developing Status*** v0.0.0.7
    package ifm ecomatDisplay _64bit Products v1.0.1.0
    package ifm PDM360NG Products v1.8.0.0

    SP9 Patch 4
    package ifm PDM360NG Products v1.8.0.0

    And for good measure, the gateway is x64 version 3.5.9.40. Any assistance with this would be appreciated.

    Click image for larger version. 

Name:	gateway.png 
Views:	24 
Size:	149.0 KB 
ID:	391

  2. #2
    Join Date
    Aug 2009
    Location
    ifm Exton, PA
    Posts
    198

    Default

    For the 1201 you will need to use the SP9 version. If you are still on the set-up screen you will need to select the load application before codesys can connect.

  3. #3
    Join Date
    Jun 2016
    Posts
    6

    Default

    Quote Originally Posted by Jeremy Kopicz View Post
    For the 1201 you will need to use the SP9 version. If you are still on the set-up screen you will need to select the load application before codesys can connect.
    That was the issue - I had selected "Load Application" while attempting to use SP15 but not at any point after switching to SP9. Thank you.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •