    Default CANOPEN Master/Slave Networks

    Hi,

    I was wondering if someone could layout best practices for network topology in terms of setting masters and slaves. Can I have more than one master on a CANOPEN network? In a CR0403/CR0451 system should the CR0403 be the master and the CR0451 be the slave? What about using only a display and several IO modules (ie. CR2032)?

    Thanks!

  2. #2
    Join Date
    Aug 2009
    Location
    ifm Exton, PA
    Posts
    196

    Default

    Depends on the display, the CR0451 is the only one suitable (at this time) to use as a master that is controlling IO. It is the only display with the 100ms watchdog timer for the IEC task. If all you are doing is looking at inputs and controlling outputs that would be considered safe, then OK. If not use a controller.

    In genereal I makle the controller the master. It is possible to have multiple masters but then this could complicate things since there would be more than one device sending NMT commands.

  3. #3
    Join Date
    Jan 2011
    Posts
    24

    Default

    Thanks Jeremy. Another question: when you add a slave element under the "PLC Configuration" section, it automatically adds the Receive PDO-Mapping, Send PDO-Mapping, and Service Data Objects tabs. Do we need to do anything with these? Your CAN networks basics tutorial doesn't address these tabs at all.
    Attached Files Attached Files

  4. #4
    Join Date
    May 2009
    Location
    Minneapolis, MN
    Posts
    300

    Default

    You can add the data in the Parameter Manager as to what is being sent and received in the PDO mapping when you use the CR0451 as a slave.

    I find it much easier to use Network Variables when passing data between a display and a controller.