    Is there an EDS file available for the CR0451 to be used as a slave?

  2. #2
    Join Date
    May 2009
    Location
    Minneapolis, MN
    Posts
    300

    Default

    There is not one currently. You could just open the template for the CR0451_Slave then go to the PLC Configuration, click on CanSlave_Device, then the Base Setting tab and have Codesys create an EDS file for you.

  3. #3
    Join Date
    Aug 2009
    Location
    ifm Exton, PA
    Posts
    196

    Default

    It would be much easier to use network variables. You don't need to add as a slave but can still do checks in your code (monitor a sent bit from each) to see if the connection is ok.

  4. #4
    Join Date
    Jan 2011
    Posts
    24

    Default

    I am using network variables. I was under the impression that I needed to add the display as a slave in order to be able to have it in the network. What template should I use for the display if I wasn't adding it as a slave to the master?

  5. #5
    Join Date
    Aug 2009
    Location
    ifm Exton, PA
    Posts
    196

    Default

    I would use the:
    ifm_Template_CR0451Layer2_V010001_02
    and layer 2 for which ever controller you are using. Much less overhead if you are not actually using the CANOpen functions.