    Default Network Variables

    I'm having issues trying to send network variable from a CR0032 to CR1081. I have the exact same set up with a CR0232 and the variables transfer over with no issues however as soon as I try to use the CR0032 there is issues.

    I'm using the CR0032 as the master and the CR1081 as the slave, I've attached images of the Object Properties for both, I've made sure all the correct information is selected based off this document.
    http://mobilecontrols.ifmefector.com...8&d=1297173353

    I'm sure there is something I need to switch in my program code to change from CR0232 to CR0032 however I'm not sure what else needs to be changed. Any help would be greatly appreciated.
    Attached Images Attached Images

  2. #2
    Join Date
    Aug 2016
    Posts
    26

    Default

    The issue was with my Baudrate, I went to Resources > PLC Configuration> CANOPEN Master > CAN parameters and had a baudrate of 125000 for the PLC for CR1081 I had a baudrate of 250000. I changed the PLC to 250000 and they communicated with no issues and the network variables were sent to the screen from the PLC.