Thread: IO Module CR203x won't work, Light flashes fast green

  1. #1
    Join Date
    Aug 2009
    Location
    ifm Exton, PA
    Posts
    196

    Default IO Module CR203x won't work, Light flashes fast green

    This is an indication that the firmware for the IO module is either not installed or not in run mode.

    Using the ifm downloader and a can adapter (PCAN is recommended) you can connect to the IO block and try placing in run mode. You will need to use the downloader tool in CAN mode.

    If placing in run mode does not work, you will need to contact ifm for instructions on how to remedy or replace the unit.

  2. #2
    Join Date
    May 2009
    Location
    Minneapolis, MN
    Posts
    299

    Default

    Set the Node ID on the IO module to F or FF (if there is one or two rotary pots for the module) and the Baud Rate to 4. In the downloader tool you can then use 125k for the baud rate and 32 for the Node ID to set the unit in RUN mode again.

  3. #3
    Join Date
    May 2009
    Location
    Minneapolis, MN
    Posts
    299

    Default

    NOTE!!!

    You can cause a unit to drop out of RUN mode by having an IO module (CR20xx) connected to a CAN device and running the downloader tool and scanning for Download ID.

  4. #4
    Join Date
    May 2009
    Location
    Minneapolis, MN
    Posts
    299

    Default

    Here is a program for the CR0451 that will also put the units back into run mode.
    Attached Files Attached Files

  5. #5
    Join Date
    May 2009
    Location
    Minneapolis, MN
    Posts
    299

    Default

    Here is a step by step using the Download Tool.
    Attached Files Attached Files

  6. #6
    Join Date
    May 2009
    Location
    Minneapolis, MN
    Posts
    299

    Default

    Here is the CAN messages needed:
    You simply need to send the 4 frames below to wake up the IO Module:

    ; Columns descriptions:
    ; ~~~~~~~~~~~~~~~~~~~~~Click image for larger version. 

Name:	maintenance.png 
Views:	47 
Size:	153.3 KB 
ID:	379
    ; +Message ID
    ; | +Cycle time in ms (0=manual)
    ; | | +Length of message
    ; | | | +Frame type: D)ata or R)emote request
    ; | | | | +Message data
    ; | | | | |
    650h 1000 8 D 2Fh 25h 10h 01h 03h 00h 00h 00h Paused
    650h 1000 8 D 40h 25h 10h 03h 00h 00h 00h 00h Paused
    650h 1000 8 D 2Fh 25h 10h 01h 10h 00h 00h 00h Paused
    650h 1000 8 D 2Fh 25h 10h 01h 02h 00h 00h 00h Paused

    0x650 ? 0x620 = 0x30 = decimal 48 = Node ID 48 = in this case

    Or use the Maintenance Tool:
    Last edited by Erik Gerrits; 01-04-2019 at 09:12 AM.